GFCI's in commercial kitchens

Status
Not open for further replies.

Jan

Member
Are GFCI's required in all outlets in commercial kitchens or just locations near water. Thanks
 
Yes, they are required everywhere in a commercial kitchen if you are under the 2005 code.

Steve
 
Ferno, there is no exception, it is all 125v 15 and 20 amp receptacles in a commercial kitchen.

Roger
 
Point out the repetitive exceptions under the dwelling unit GFCI requirements - Every location where a single receptacle is permitted instead of a GFCI is specifically referenced. Note the differences in the exceptions among the different locations.

Note the lack of exceptions in a residential bathroom - all 120V 15A & 20A receptacles require GFCI protection.

You are right. :)
 