GFI Equipment breakers

Status
Not open for further replies.
Are you proposing using 30ma GFPE in lieu of 5ma protection that is required on receptacle circuits?
 
yes because the the 5 ma seem to trip easy on a cooler and heating elements and if i am reading the code right the 5 ma if for counter receptacles not equipment that stays plugged in
 
Sounds like commercial refrigeration equipment is calling for GFP protection, or someone wants to include it.

Most 120v readings I find at energized refrigerator door handles are caused by defective light sockets or light switches.

By the time I get there, workers were accustomed to working in the dark, using their phone flashlight, and bibs to grab the door handle.

Its not until the owner himself grabs the door with his bare hands, and gets jolted on his butt, before someone finally calls.
 
yes because the the 5 ma seem to trip easy on a cooler and heating elements and if i am reading the code right the 5 ma if for counter receptacles not equipment that stays plugged in

You're reading it incorrectly, all receptacles in this location require GFCI protection (5ma, class A) whether they feed permanently installed equipment or counter receptacles.
 