I was failed on a final inspection for the 2 outlets on the nook counter top (mail center) not being GFI protected. Inspector gave 210.52 B3 and B1. What am I missing?
 
Re: GFI for nook counter top?

Are these receptacles serving the kitchen countertops? If so 210.8(A)(6) 05' NEC should be quoted.
 
Re: GFI for nook counter top?

The code section requiring kitchen outlets to be GFCI protected is 210.8(A)(6)Kitchens-where the receptacles are installed to serve the countertop surface.

Is the "mail center" in the kitchen? If so then the inspector may be right.

Chris
 
Re: GFI for nook counter top?

It is NOT in the kitchen. It is in a room with lower ceiling than the kitchen just off of the kitchen and the plans call it a nook. There is also a wet bar with counter in that room with GFI outlets.
 
Re: GFI for nook counter top?

Ok 210.52 (B) 1 and 3 Yes granted on small appliance circuits but the picture You have painted us then NO gfi protection is required.
 
Re: GFI for nook counter top?

I say the inspector is off. If you have more than 6' from the bar sink to the mail center outlets, then GFI protection is still not required.Ron
 
Re: GFI for nook counter top?

This sounds like an "other than dwelling" kitchen. (B)(3) & (B)(1) are for the rooftop and bathroom???

Is the nook part of the kitchen on the plans? It would be hard for us to tell if you are not sure.
ALL, ALL 125 volt 15 & 20 ampere receptacles in the kitchen will require GFCI protection under the 2002 & 2005 NEC. 210.8 (B)(2) ['05 NEC]
 
Re: GFI for nook counter top?

Originally posted by pierre:

ALL, ALL 125 volt 15 & 20 ampere receptacles in the kitchen will require GFCI protection under the 2002 & 2005 NEC. 210.8 (B)(2) ['05 NEC]
Even the refrigerators, disposals, dishwashers, and trash compactors?

[ January 23, 2006, 06:51 PM: Message edited by: celtic ]
 
Re: GFI for nook counter top?

Originally posted by sllazar:
There is also a wet bar with counter in that room with GFI outlets.
The plot thickens...
How far from the bar are the devices?
210.8(A)(7) [2002 NEC]
 
Re: GFI for nook counter top?

Originally posted by celtic:
Originally posted by pierre:

ALL, ALL 125 volt 15 & 20 ampere receptacles in the kitchen will require GFCI protection under the 2002 & 2005 NEC. 210.8 (B)(2) ['05 NEC]
Even the refrigerators, disposals, dishwashers, and trash compactors?
Yes in commercial kitchens that is the code.
 
Re: GFI for nook counter top?

sllazar

Dwelling unit or 'other than dwelling unit'

I agree with Pierre a 'mail center' doe not sound like a dwelling.
 
Re: GFI for nook counter top?

I interpreted it as being in a dwelling unit, and being a place to store or handle the household mail, to pay bills, and to drink coffee, all in close proximity to the kitchen.

My read is that 210.52(B) applies, and that these receptacles are part of the Small Appliance circuits. My read is also that 210.8(A)(6) does not apply, and GCFI is not needed.
 
Re: GFI for nook counter top?

The wet bar is more than 10 feet from the counter in question and seperated by a door way. As you enter the house from the garage you go into the laundry room, and then into a short hall. At the end of the hall on your right is the nook. On the left is the kitchen with an island. So the way I look at it the kitchen and nook are seperated by the entry to the house from the garage. Just the way I see it. I think the big issue here is that 210.52 B1 and B3 Are in referance to Small applicance outlets and Required outlets, not GFI Protection. That would be 210.8A 1 thru 8.
 
Re: GFI for nook counter top?

Originally posted by iwire:
Yes in commercial kitchens that is the code.
But the OP failed in a 210 reference...dwelling units.

Why are we off a tangent?
 
Re: GFI for nook counter top?

Originally posted by sllazar:
Just the way I see it.
I'd like to see it.
Any chance of getting an image uploaded - even if only paper and pencil?
 
Re: GFI for nook counter top?

Originally posted by sllazar:
I was failed on a final inspection for the 2 outlets on the nook counter top (mail center) not being GFI protected. Inspector gave 210.52 B3 and B1. What am I missing?
Providing the nook receptacles are not in the room classified as the kitchen, then they should not have to be GFCI protected. Another example of this is dining room receptacles; they can be part of the small appliance circuit but are not required to be GFCI protected.
 
Re: GFI for nook counter top?

How this went to commercial kitchens is a mystery.


I see no need for gfci protection for these receptacles as you have explained their installation.
 
Re: GFI for nook counter top?

Originally posted by sllazar:
I was failed on a final inspection for the 2 outlets on the nook counter top (mail center) not being GFI protected. Inspector gave 210.52 B3 and B1. What am I missing?
Everything's confused on this one.

The only logical reason to cite 210.52(B)(1) is if the receptacles in the nook were not on small appliance branch circuits. They should be.

Those receptacle circuits can only serve the areas defined in 210.52(B)(1). Did you comply with this?

As for the GFI bit, not required.

I'm wondering if the tag is illegible? No offense, fellas, but some inspectors have atrocious penmanship. There's been many a holy tangent cut short by realizing the tag didn't really say what I thought it read. :D
 