210.8(A)(6)Originally posted by sllazar:
What am I missing?
Even the refrigerators, disposals, dishwashers, and trash compactors?Originally posted by pierre:
ALL, ALL 125 volt 15 & 20 ampere receptacles in the kitchen will require GFCI protection under the 2002 & 2005 NEC. 210.8 (B)(2) ['05 NEC]
The plot thickens...Originally posted by sllazar:
There is also a wet bar with counter in that room with GFI outlets.
Yes in commercial kitchens that is the code.Originally posted by celtic:
Even the refrigerators, disposals, dishwashers, and trash compactors?Originally posted by pierre:
ALL, ALL 125 volt 15 & 20 ampere receptacles in the kitchen will require GFCI protection under the 2002 & 2005 NEC. 210.8 (B)(2) ['05 NEC]
But the OP failed in a 210 reference...dwelling units.Originally posted by iwire:
Yes in commercial kitchens that is the code.
I'd like to see it.Originally posted by sllazar:
Just the way I see it.
Providing the nook receptacles are not in the room classified as the kitchen, then they should not have to be GFCI protected. Another example of this is dining room receptacles; they can be part of the small appliance circuit but are not required to be GFCI protected.Originally posted by sllazar:
I was failed on a final inspection for the 2 outlets on the nook counter top (mail center) not being GFI protected. Inspector gave 210.52 B3 and B1. What am I missing?
Everything's confused on this one.Originally posted by sllazar:
I was failed on a final inspection for the 2 outlets on the nook counter top (mail center) not being GFI protected. Inspector gave 210.52 B3 and B1. What am I missing?