Even then, you would still need a GFCI receptacle at every location, due to the shared neutral. The feed through feature would not work. A GFCI breaker is a quick and easy solution, and the most logical, IMO.Originally posted by indcom:
I would suggest that would wirenut 1 of the circuits to feed thru to the next box and so on down the line until you could install GFIC devices at each location and GFIC protect those further down the line.
I would definitely not mess around with the boxes if you have alumninum wire. That is a can of worms.Originally posted by 1793: Thanks for the explanation. I think I'm going to have trouble with using the GFCI Receptacle in the existing counter boxes. Each has 2 12/3 AL cables. I would need to add wirenuts and pigtails and the?device as well, unless I've missed something there would not be enough room for all of the necessary connections and the device. The boxes are nail-up Bakelite(?). Since the panel is twined out, what about setting a sub-panel and using a 2 pole GFCI breaker?
Was the guy hot?Originally posted by 1793:
I thought I was going to have to perform CPR.
It depends on how you wire the circuit(s).Originally posted by aelectricalman:
Ok, I have checked this whole post and I dont believe I have seen this, but Ill ask anyway. What problem might arise if I use a 12-3 wire to feed two kictchen circuits. With both having to be GFCI protected, will this set-up work. What problems could occur due to sharing a neutral.