GfI Needed for A 208V 30Amp AC Recepticle?

Status
Not open for further replies.

ssadvis

Member
A 208V 30Amp recepticle dedicated to a AC unit is located less then 6' from a sink in a commercial kitchen. Is GFI protection needed required by code.
 
No. GFCI protection is only required for 125 volt receptacle outlets rated at 15 or 20 amps. Reference: NEC 210.8.
 