S ssadvis Member May 18, 2007 #1 A 208V 30Amp recepticle dedicated to a AC unit is located less then 6' from a sink in a commercial kitchen. Is GFI protection needed required by code.
A 208V 30Amp recepticle dedicated to a AC unit is located less then 6' from a sink in a commercial kitchen. Is GFI protection needed required by code.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer May 18, 2007 #2 No. GFCI protection is only required for 125 volt receptacle outlets rated at 15 or 20 amps. Reference: NEC 210.8.