Originally Posted by Dave6
Anyway I wired up a test board with 2 GFCIs in series and it works fine. I kinda answered my first question there. But, what has changed? Why does this work now? All 3 of us are curious and would of bet against this working.
Why would you wire GFCI's in series. We are not talking about series connections but parallel. A GFCI feeding another GFCI recep. or plug should not cause any tripping unless there is a problem with one of the units.
Let me explain a little more...First, completely agreed that this is stupid, no reason to etc. I believe we are on the same page there. The reason is our EE wants us to. Because he is interperting the code incorrectly and is convinced that every outlet in these bathrooms needs to be a GFCI. He is not grasping the GFCI protected concept. So...my plan to show him it wouldn't work was to make a test board with two in series. This is based on something I learned the hardway 15+ years ago when I put two in series and the first one in line automatically tripped. I called my boss at the time to ask why, he cussed me out and told me to take the second one out. Two other electricians I work with had similar experiances back in the day and all were taught that two GFCIs can't share the same neutral in series. What has changed with GFCIs to allow them to be put in series? We have a couple theories...but all 3 of us our curious and confused.
I think that about covers it...This is probably going to be a case of agreeing with the EE, then doing the right thing in the field.