- Massachusetts
At this point, the easiest and most cost effective solution is what Larry posted.
It sure is.
What is the code reference in this case?There sure are, but disconnecting means are not.![]()
Some disconnects are required to be "accessible".
Accessible can be behind equipment that is not guarded by locked doors, elevation, or other effective means, as per the definition in Article 100
I'm doing a quick breakfast before heading to work, so I don't have a code book to look this up. But does an appliance need a local disconnecting means in the first place?
I mean that a plug and cord connection certainly does allow for easy disconnection for maintenance, but if the receptacle is hard to get at, why should that matter?
422.33(B) addresses ranges specifically.
More specifically - Electric ranges
I installed one of these and the outlet is right where they instruct it to be ,. No breaker lock was installed . the gas connection is flexible so it is accessible to those who would service the range .
I was able to move it myself.
IMO you have a violation.
It does not matter where the instructions say to place the receptacle, your more then free to install the receptacle behind the range but if you also want it to serve as the disconnecting means you have a problem.
Let me ask this, how big or heavy does an appliance have to be before I can not block the disconnecting means with it.
Can I place the disconnecting means for a commercial dishwasher behind it so that the dishwasher has to be removed before the switch can be operated?
I think what we have a here is a section of code that has always worked using a 'common sense' approach but once we really think about it has a lot of holes.
Bob,
Not to tak the wind out of your sale but the PDF above showes the Gas and electric below. What is the problem here. The cord and gas shut-off will be accessable when you remove the drawer. I do electric ranges like this all the time. What is the problem it is very easy to remove the plug. It's far less likely to be damaged in a cabinet full of pots and stuff.
Maybe you are a gorilla.
If it was hardwired would you locate a disconnecting switch behind it?
No ..
do you install a breaker lock for the fridge if the receptacle is behind it ?
Thanks for the code articles. But I have to take issue with you on this one, Bob. It says "accessible," not "readily accessible." The definition of "accessible" speaks of being closed in by the structure, not of moving an appliance out of the way.It has to be 'accessible' per 422.33(A)
True. But it doesn't say the same thing about gas ranges with 120 volt accessories.If I have an electric range without a drawer the NEC seems to feel the disconnect would not be accessible.