and yup,.. you guessed it ,..2010 ROP
It is very unlikely that it is a violation.
But Bob feel free to submit a proposal
just because he's been shot down four times is no reason for you not to try.
It is very unlikely that it is a violation.
But Bob feel free to submit a proposal
17-27 Log #1800 NEC-P17 Final Action: Reject
(422.33(A) and (C))
_______________________________________________________________
Submitter: Dan Leaf, Seneca, SC
Recommendation: Revise last sentence of (A): Where the separable cord
connector, plug and receptacle or flanged surface device are not readily
accessible, cord and plug connected appliances shall be provided with
disconnecting means in accordance with 422.31.
Revise (C): The rating of an attachment plug, a receptacle, or a separable
cord connector or flanged surface device shall not be less than the rating of any
appliance connected thereto.
Substantiation: ?Accessible? as used in (A) appears to apply to equipment.
Receptacles are required to be accessible and the disconnecting means of
422.31 are required to be accessible.
(C) should include attachment plugs and flanged surface services.
Panel Meeting Action: Reject
Panel Statement: CMP-17 does not accept the changes to the wording as there
is no improved clarity with respect to the word ?accessible? applying to the
separable connector, plug, and receptacle.
Number Eligible to Vote: 13
Ballot Results: Affirmative: 13