gfi on arc fault

Status
Not open for further replies.
Mustang, just curious, where are you located? Might it be somewhere on the east coast of Fl?

Roger
 
In response to OP, it might be a local code requirement. I know when I was working out west they had a local code where you were not allowed to feed anything else off your AFCI ckts. But like eveyone said there's nothing in the code that prohibits it.
 
1968mustang said:
I had an inspector fail me for having an outside gfi receptacle tied to a bedroom arc fault breaker. I talked to some other electrician and they too have not heard of this being a code violation. Any information would be greatly appreciated.

Just curious?
Was this a rough in? or a final?
I can't see how he would notice this on a final.
Forget about the code reference, as it don't exist.
But for common sense why would one affect another?
 
Mustang, along with all saying it is allowed in this thread, see the first question and answer HERE for another yes.

Roger
 