Question: Does section 210.8 of the electrical code prohibit a 125-volt, single phase, 15- or 20-ampere GFIC receptacle from being installed in a crawl space because the receptacle is not “readily accessible” from the normal occupied areas of the dwelling?
Answer: A GFCI receptacle located in a crawl space is not typically readily accessible from the normal occupied areas of the dwelling. Outlets located in normal occupied areas of the dwelling that possess GFCI protection located within the crawl space creates a hindrance to the occupants when such GCFI protection must be reset from within the crawl space. However, a GFCI receptacle is typically readily accessible from within the crawl space where such receptacle is being utilized for servicing HVAC or plumbing equipment. Therefore, a GFCI receptacle is allowed in the crawl space if the GFCI only protects the outlet(s) within the crawl space. Nothing in this document is meant to suggest that the branch circuit supplying the GFCI protected receptacle(s) within the crawl space is prohibited from also supplying outlets in the normally occupied areas of the dwelling. Additionally, nothing in this document is meant to suggest that the GFCI protection for the receptacle(s) in the crawl space must be located within the crawl space.