GFI outlet ok for gas range

Status
Not open for further replies.

mpbass5

Member
Hello, I am new to this site and i was hoping to get an answer about an electrical code. I am in the process of selling my condo, the buyer just had an inspection done and the inspector stated that the gas range is currently plugged into a GFI outlet and that it should be plugged into a non-GFI dedicated outlet. This didn't make sense to me? Is the correct? What is the code on this? Thanks for your help
 
Oooops, misread your post so this is an edit. There is nothing wrong with plugging it into a GFCI receptacle or circuit.

Roger
 
Last edited:
What is the code on this? Thanks for your help
It is allowed to be on the SA branch circuit.

(2) No Other Outlets. The two or more small-appliance branch circuits specified in 210.52(B)(1) shall have no other outlets.
Exception No. 1: A receptacle installed solely for the electrical supply to and support of an electric clock in any of the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power for supplemental equipment and lighting on gas-fired ranges, ovens, or counter-mounted cooking units.
Rick
 
I think that inspector may be thinking of how some time ago the ignitor units on some gas ranges caused nuisance trips of GFCI's.

But as stated above it's perfectly ok by Code.
 
... the inspector stated that the gas range is currently plugged into a GFI outlet and that it should be plugged into a non-GFI dedicated outlet. This didn't make sense to me? Is the correct? What is the code on this?

What type "inspector" was this?
I'm guessing a "home inspector" hired by the buyer ~ correct?


How did the "inspector" answer your questions about what code this is in?
 
Yes, it was a home inspector hired by the seller. My guess is that he had to find something wrong with the place since he was getting paid to do it. I did not have a conversation with the inspector, I just received an email. There were a few more "suspect" things that he added. My guess is that he needed to put something down on the report and didn't think I would research it. Oh well, guess he didn't get to pull a fast one. Thanks again for everyone's help
 
I normally don't install the range receptacle off the load side of a GFI but I recently did a kitchen remodel where I did so for convenience in wiring. The woman began having problems when the electronic igniter began tripping the GFI receptacle. Then the appliance repairman came in and told her that having the range connected to a GFI receptacle would damage the range.:confused: I had to go back to install an additional GFI receptacle and wire the range receptacle off the line side of the GFI.:mad: I wish I was as smart as an appliance repairman.:grin:
 