You did'nt specify whether this was a dwelling or recreational.if it's the latter then the inspector was correct.sparky90 said:Do you need GFI protectionf for a recessed light fixture in a bathtub/shower stall? And if so where in the NEC is it.
RUWired said:You did'nt specify whether this was a dwelling or recreational.if it's the latter then the inspector was correct.
551.53(B)
(B) Shower Luminaires (Fixtures) If a luminaire (lighting fixture) is provided over a bathtub or in a shower stall, it shall be of the enclosed and gasketed type and listed for the type of installation, and it shall be ground-fault circuit-interrupter protected.
Rick
charlie b said:The requirements for GFCI protection are in 210.8, and they only talk about receptacle outlets.
stickboy1375 said:Yes, but some light manufactures require it...
infinity said:Can you name one? I've never seen a fixture that required GFCI protection in a tub area.
Dennis Alwon said:I have not seen a light that requires GFCI either but there are fan/lights that require GFCI when installed over a tub-- manufacturers requirement not NEC.
Energize said:?????
The "recreational" you are referring to is under part 4 of the Recreational Vehicles and Recreational Vehicle Parks Article of the NEC.
infinity said:Can you name one? I've never seen a fixture that required GFCI protection in a tub area.
electricguy61 said:
stickboy1375 said:Anyone have any clue why a fan/light does require GFI protection?