WE ARE DESIGNING A 13800V PRI WITH 240 V DELTA SEC
SERVICE AT 3000A FOR RESEARCH FACILITY, DOES THIS REQUIRE A GFI PROTECTED MAIN BREAKER, IF SO HOW DOES IT REFERENCE THE NODE.
The requirement in 240.13 is for solidly grounded wye electrical systems of more than 150 volts to ground. It looks to me like your delta system would be exempt from the ground fault requirement. Although I still don't node exactly what node you are refering to.
they do a lot of goverment work for subs they are testing a sleeve for the periscope and they use voltages similiar to what equipment might use, they selected the delta system and voltage