har har
that must get some attention =0
so i have made "all" the mistakes with gfi's that i can think of :angel:
but this one has me scratching my emojicon:?
tea shop with two circuits only on the countertop
report is that the gfis keep tripping
i go there and cant replicate the fault
further investigation says they mostly trip in the morning when certain appliances are bringing the water up to temp
but i ran all the appliances really hard when i was there and couldnt replicate the fault - tripped the 2p breaker before the gfis [middle pair on 25quad]
mwbc feeds the counter and the gfis are pigtailed to the shared neutral and one power leg
so my thinking is
that the water heating appliances may exhibit some internal fault mostly in the morning when they come up to temp
or
that some voltage imbalance is bothering the gfis at a certain time of day being there are a bunch of mwbc at that counter -
powering the undercounter fridges
but i originally ruled that out because i had steady power off the pigtail [shouldnt care much about beyond the pigtail]
or
in the morning they are doing some water cleaning action at the counter and that is getting in the plug connection
action takenI replaced the gfis with new WR and TR units
Here is the bizarre key: the 2nd GFI [leviton] i replaced failed immediately out of the box - a very rare occurance- [[in the last 20 years was the last time that happened]]
right out of the box it would would trip immediately - BUT only when connected to the ground
### so i thought "ahha! must be some bootleg ground touching here"
but i didn't see that in the box - so i tried replacing the unit [troubleshooting for people in a hurry] and it "seemed ok to me"
so i chalked up the erratic behavior to a bad device - but i didnt really trust that judgemnet
###and now i have a callback in the morning - want to get some consensus on my way there
there was no voltage between N-G during the interval i measured
any idears?
I need to be able to replicate the fault where the gfi opens
<B>Fig. 1.</b> All 15A and 20A, 125V receptacles located in an area with a sink and permanent facilities for food preparation and cooking must be GFCI protected.
so my thinking is
or
or
any idears?