Hello,
I have a question regarding GFI circuit breakers. We currently have a situation that is kind of unique and want to get some thoughts. We have a 3 phase system that is an old antiquated grounded B phase system. We use 240 volt single phase power to power 4 receptacles which come from 4 standard 20a breakers on a machine and some of these receptacles reference A-B , B-C and A-C for balancing as we have over a 125 machines with this setup. We are looking at installing a 2 pole GFI breaker for each of these receptacles which i see requires a neutral to the breaker for the electronics. However, the grounded B system does not have a neutral with it. We do have a control transformer on the machine that steps down the 240 to 120v with a neutral to run the 120 v power on the machine. So my question is two-part. First. Do you think the GFI would work correctly if the neutral on the breaker was tied to this secondary neutral. Second, if this did work, if the breaker was tied across A-B phase would it function properly as well if the one phase is grounded. In this system we measure 240v to ground on phase A and C but 0 volts to ground on B phase. My preliminary thought is this grounded phase may trip the breaker as it will think it is a ground path. Possibly a secondary transformer install would isolate the grounded B phase but unsure of that either. Appreciate any thoughts on this scenario. Thx