GFI receptacles

Status
Not open for further replies.

sleepy

Senior Member
i have been told that in a public assembly use building gfi receptacles cannot be grouped together. i looked in section 518 and could not find anything. please help, thank you
 
Re: GFI receptacles

What do you mean by grouped together? Do you mean more than one GFI on the same circuit, a GFI feeding down stream devices?
 
Re: GFI receptacles

the first receptacle is a gfi and then downstreem we have other gfi's and regular.
 
Re: GFI receptacles

As long as they are wired correctly this shouldn't be a problem! Your just sharing a circuit to more than one place. This would just be branch circuit wiring, pretty common. Never heard of any requirement for places of assemble that would disallow this.

Edited to add:
Someone may be getting the requirement for dwelling unit bathroom, that require an individual branch circuit that shall have no other outlets, mixed up with your situation. I assume your are talking about a commercial building.

[ June 06, 2005, 01:36 PM: Message edited by: guesseral ]
 
Re: GFI receptacles

It sounds like you have alot of GFI's in this building.
or is the plan check requiring seperate circuits to ea. restroom (probably 1 Recept.ea.restroom)
and maybe a circuit for 1 or 2 Ext. recepts.

I don't understand :confused:
 
Re: GFI receptacles

Originally posted by sleepy:
the first receptacle is a gfi and then downstreem we have other gfi's and regular.
Just off the top of my head, it's not a great idea in restrooms, because then the men will keep tripping the GFI with a tester to go into the ladies bathroom. But other than that... :D
 
Re: GFI receptacles

Originally posted by sleepy:
the first receptacle is a gfi and then downstreem we have other gfi's and regular.
In other words, there is a GFCI downstream from another, cascaded. I don't know it to be illegal, but there's no good reason to do so, and a couple of reasons not to: cost, and troubleshooting.
 
Re: GFI receptacles

If you have 2 or more GFCIs in the same box they do need to be TAPED particularly when using stranded wire. Learned that the hard way during spring break in 1987 when doing a panel change.

Unlike rich kids I had to do things such as hot panel changes curing spring breaks back in college. Of course, I have always wondered how the rich kids get high buck summer jobs or otherwise get their wallet.
 