They make GFCIs with a built in alarm.The exception that permitted using a single receptacle for a dedicated appliance in lieu of GFCI protection last appeared in the 2005 code. If you are on a newer code, the receptacle must have GFCI protection. With refrigerators and freezers that do not have power conversion equipment (VFDs) a tripped GFCI most often indicates a problem with the equipment.
You could add an alarm to get a notification of loss of power to the freezer.