i guess ive been confused how gfci works , i thought it measured the conductors seperately they must be equal in the hot lines or the difference will be in the neutral. according to what I see if you put a clamp on meter on all the hot and neutral comming in together it should cancell the current and read zero unless there is a leak thats not returning. I still dont understand what all the other wires are doing in the doenut hole , There are a lot more wires than the 3 lead in conductors.
any current passing through the CT on one conductor must again pass through on a return conductor or the CT will read current and operate the trip device. does not really matter what they go to to some extent.