GFI

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
Re: GFI

As far as the NEC is concerned as many as you want, 1,10,100 GFCIs.

I have heard that some manufactures have limits but have never seen this myself.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: GFI

Jhc, is the question how many can you put on a 20 amp circuit, if so, follow Bobs info and go with as many as you want. (residential)

If the question is "how many can you put down stream of a GFCI device" why would you, the first one would guard the rest. :D

The answer would still be as many as you wanted as far as the NEC. If a manufacturer limited downstream devices, this limit would have to be adhered to per their instruction.

Roger
 

bphgravity

Senior Member
Location
Florida
Re: GFI

Yes, Bob is correct. The code soes not specify and maximum receptcles on a circuit, it just specifies the total load that can be seen on any one circuit.

It obviously would not be a good design to put more than just a few receptacles on any circuit, gfci protected or not.

Some GFCI receptacle manufacturers do specify maximum downline receptacles that should be placed on one circuit. Manufacturers directions must be followed per the NEC. :)
 

bennie

Esteemed Member
Re: GFI

Bob is correct. The question never comes up because who would want to put more than one?. This is like putting 10 stamps on a letter just because you can.
 

jhc8796

Member
Re: GFI

Thanks for the help guys, but reason I asked the question was I installed 3 GFCI,s recpts on the outside of a agriculture shop this week and my forman said only one GFCI on a 20/amp ckt I thought he was wrong.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: GFI

Originally posted by jhc8796: ? my foreman said ?.
Do you mean that your foreman told you that more than one would violate the NEC? If so, your foreman was wrong (as others have already pointed out). Do you mean that your foreman told you that "only one" is standard industry practice? If so, your foreman was wrong (as others have already pointed out). Do you mean that your foreman told you it would violate local codes or local jurisdictional rules? If so, we can?t contradict that statement without seeing the local codes and rules. Do you mean that your foreman told you it would violate the contract requirements? If so, we can?t contradict that statement without seeing the contract. Do you mean that your foreman told you that his or her experience shows this installation to be in the best interests of the owner? If so, then I, at least, would tend to disagree with this assertion.

I go through this exercise to invite your attention to something I?ve seen many times in this forum: If ?someone says,? then ask them to state their source. Then you will have the ability to verify the source, and decide for yourself.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: GFI

Bob, do you hear that Twilight Zone music? :D :D :D
 

jhc8796

Member
Re: GFI

Thanks Charlie, glad I got this info it will save me from arguing with my forman whom claims to know it all. :D :D
 
Re: GFI

your not talking about having gfi devices downstream from one another......
only reason I ask is I just ran into a situation with a homeowner who was replacing old receptacles
(agree w/ foreman comment
 

bill addiss

Senior Member
Re: GFI

jhc,

Here's something else to look at.
None of the components in an Electrical System is perfect. They all have a certain amount of inherrant 'leakage'. Manufacturing specs are such that the 'leakage' is kept below a certain level, but if you add enough 'leaky' items together you will, at some point, have enough to cause tripping of a GFCI.

So, a fine point, but there must be some practical limit to the quantity of components that can be downstream of a GFCI. But there are too many variables to put any numbers to it.

To echo the others, only one GFCI is needed for the circuit if everything is connected downstream.

Bill
 

pierre

Senior Member
Re: GFI

Hello Bill

In reference to the 'leakage'in GFCI circuits, I received a call the other day from a contractor who had installed a timeclock for a pool. It was tripping the GFCI, he went and purchased another and it tripped again. The timeclock was about 130 feet from the GFCI Breaker. I suggested he install the GFCI closer to the pool pump and he did. It worked fine. I learned about this on this forum. Thanks for making me look good!!!

Pierre
 

jhc8796

Member
Re: GFI

Yes Bowman gfi,s downstream because they were all on the outside exterior wall. What do you disagree with that installation if so please explain so I will know.
 