I'm working on an industrial project. The owner's production equipment manufacturer (located in Europe) sent us the following request:
"General remark concerning the protection of the power supply:
Due to the servo motors installed in the machine, during startup of the machine or while the servo drives are in motion, leakage currents will appear. This is technically caused and no error. Because of these leakage currents the power supply protection must be as follows:
We recommend the installation of a RCD (RCD = Residual Current protective Device). This must be a selective FI switch. This is a slow type for the use of devices with power filters. It has to be a Type B RCD (sensitive to all currents), with a medium sensitivity (MS) or low sensitivity (LS), typically for protection of machine. More information: http://en.wikipedia.org/wiki/Residual-current_device "
Best I can tell, they are asking for the disconnect feeding their equipment to be provided with Ground Fault Protection. But what I don't know is if I have to specify something special to meet all of their requirements? The circuit is 480V, 20A, 3Ph. Load is 5kW.
"General remark concerning the protection of the power supply:
Due to the servo motors installed in the machine, during startup of the machine or while the servo drives are in motion, leakage currents will appear. This is technically caused and no error. Because of these leakage currents the power supply protection must be as follows:
We recommend the installation of a RCD (RCD = Residual Current protective Device). This must be a selective FI switch. This is a slow type for the use of devices with power filters. It has to be a Type B RCD (sensitive to all currents), with a medium sensitivity (MS) or low sensitivity (LS), typically for protection of machine. More information: http://en.wikipedia.org/wiki/Residual-current_device "
Best I can tell, they are asking for the disconnect feeding their equipment to be provided with Ground Fault Protection. But what I don't know is if I have to specify something special to meet all of their requirements? The circuit is 480V, 20A, 3Ph. Load is 5kW.