Greentagger
Senior Member
- Location
- Texas
- Occupation
- Master Electrician, Electrical Inspector
Trying to figure out how 230.95 would apply to ground fault protection for a 1200A fusible service disconnect for a 277/480V solidly grounded wye system. If it’s to protect equipment, how is that accomplished through fuses. Noted on plans there is to be a ground fault indicator to be installed in a readily accessible location. Also appears load side of fused 1200A service disconnect feeds a 1200A I Line breaker which appears to have GFP settings on it? Is this what is protecting the disconnect? Maybe that makes sense. I’ve heard of bolted pressure switches. Don’t really understand this concept. A little help please. Thanks.