While Art 230.95(C) is clear on testing, it is not so clear as to who is required/qualified to do it. Do you think it is reasonable for an AHJ to require a quilified 3rd party or manufacturer do this testing for compliance?
Do you have the equipment to perform the testing?
We test GFPE sysyetms for other ECs, typically a small high current test set will set you back $8,000-$10,000, there are aditional test we perform as part of the acceptance test. We megger the switchboard, line, load, line to load of the CB/switch and megger the neutral with the neutral to ground disconnect link removed, lastly we ductor/Micro-ohm the power contacts.
I know a few EC's that do their ow testing.