We're doing a factory dismantle and rewire, and ran into a weird one today. Both electrical rooms have capacitor banks, and all MDP breakers have been de- energized except to the house lighting panel and a few others. Breaker feeding MCC-3 is off and locked out. We have detected voltage intermittently in the feeds to that MCC. Weird voltages too (A-B 200V, A-C 212V, B-C 12V, A-G 278V, B-G 76V, C-G 66V). All downstream switches and breakers are open on MCC-3, voltage persists, so it seems to be coming from the line side in the MDP. Cap bank breaker is open, as well as feed breaker to MCC-3. Levels seem too high for induction. Any other ideas? Also, voltage readings go to zeros for no discernible reason. Literally witnessed it tested at zero, left the site, and my guy called me back to show me the voltage reasons in- person. Where is this backfeed coming from?!?