Ghost voltage in an MCC
dweekly07
New User
Iowa
Safety
We're doing a factory dismantle and rewire, and ran into a weird one today. Both electrical rooms have capacitor banks, and all MDP breakers have been de- energized except to the house lighting panel and a few others. Breaker feeding MCC-3 is off and locked out. We have detected voltage intermittently in the feeds to that MCC. Weird voltages too (A-B 200V, A-C 212V, B-C 12V, A-G 278V, B-G 76V, C-G 66V). All downstream switches and breakers are open on MCC-3, voltage persists, so it seems to be coming from the line side in the MDP. Cap bank breaker is open, as well as feed breaker to MCC-3. Levels seem too high for induction. Any other ideas? Also, voltage readings go to zeros for no discernible reason. Literally witnessed it tested at zero, left the site, and my guy called me back to show me the voltage reasons in- person. Where is this backfeed coming from?!?
Probably a mistapped neutral somewhere. Turn off the panels you still have energized one by one to see if the voltage goes away, then if one panel seems to be the culprit, go through turning off six breakers at a time until a group is found, then narrow it down again. Divide and conquer!
I have carried an analog meter for this problem. My ol' Radio Shack about 40 years old.
Does that old meter have a Category rating? I know my old Wiggy did not, so my safety department made me stop using it.
I doubt that.
What's the problem with "wiggies"? I never had one. I did have an Amprobe though.
The problem is not genetically wiggies. The issue is being the correct safety category, which often requires fusing.