Girdling

Status
Not open for further replies.

TheJed

Member
When grounding conductors are run through metallic conduits or metallic clamps are used, you get the result of girdling.
Does this pertain to unshielded ground conductors? What if the ground conductor is shielded. Isn't this essentially the same thing with a conductor inside the shield that's inside a metallic conduit? Would it be double the girdling effect?

Any reference to unshielded or shielded wert girdling?

Thanks
Jed-
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The issue of increased impedance for a single conductor of an AC system only occurs where that single conductor is run through ferrous materials. Shielding is not a ferrous material.
 