So, i was reviewing questions I had written for my 2nd year apprenticeship. I Was making sure I had the proper reference from the book I was teaching. I didn't like the way the words were in the book and I though about deleting the question. First I decided to check the code book and found out that my teaching book was merely taking its bad from the NEC. Here is the Question:
After reading the code book definitions, I realized that either answer a. is correct period. b. is correct if you are reading the definition of Service Conductors, but not if you are reading the definition or Service conductors Overhead so c. is ambivalent and d is always wrong.
- Which of the following are considered Service Conductors?
- The conductors attached to the utility transformer and extending underground to the building it is feeding. Terminating in a gutter.
- The insulated conductors run in conduit or cable extending from the service head to the service disconnect, including the portion between the meter and the disconnect
- Either 1 or 2
- None of the above
After reading the code book definitions, I realized that either answer a. is correct period. b. is correct if you are reading the definition of Service Conductors, but not if you are reading the definition or Service conductors Overhead so c. is ambivalent and d is always wrong.