wbdvt
- Rutland, VT, USA
- Electrical Engineer, PE
I couldn't tell you if the picture was a joke, but when talking arc flash protection we are talking protection from burns from the heat produced in the arc incident. That heat is measured in calories.
One calorie is the amount of heat needed to raise one gram of water 1 degree C.
Actually for arc flash it is incident energy not heat. The unit of measure is cal/cm2 (calories per square centimeter).
The definition of Incident Energy from NFPA 70E-2015: The amount of thermal energy impressed on a surface, a certain distance from the source, generated during an electrical arc event. Incident energy is typically expressed in calories per square centimeter.
Whereas the correct definition of heat refers to the transfer of energy between particles in a system and this is measured in calories. Temperature on the other hand is a measure of how much energy is in that item. So if one has a hot iron, that iron has a lot of energy in it (temperature) and touching it transfers that energy to your hand (heat).
So the 27 cal label on the gloves means that touching the glove will transfer 27 calories to your hand in the form of heat. I wouldn't want to touch that. :happysad: