The specs say the inverter output is 9.6 kW, so you had to dial that back to 7.7 kW because you only had a 40A feeder available?This setup is on a 40A detached garage circuit.
Pretty sure you are required to do that, all of the applicable NEC sections treat the inverter output current as a continuous current and require OCPD sizing of at least 125% of that current, unless you are using 100% rated OCPD (which don't exist at this rating). E.g. 2023 NEC 706.31(B)@wwhitney I did not. Consumption won't exceed the output rating.
Yes, on the link in post #2, at the bottom you have to select the second tab (internal to the web page rendering) to see the specs on that inverter.Looks interesting, so does the car just output DC and one of those boxes is a special inverter for the car DC?
Sorry for the dumb questions, you mean post #5?Yes, on the link in post #2, at the bottom you have to select the second tab (internal to the web page rendering) to see the specs on that inverter.
Cheers, Wayne