Gonna set my house on fire?

Status
Not open for further replies.
Did this install today on my home. How'd I do?

I asked an old electrician and he said that I ought not to mix the Neutral with the Ground at the main like that cause "it could cause problems", though he did not give further detail. But if the Neutral and Ground Bus are bonded in the main anyway (which they definitely are on this panel), what does that matter? I used the ground bus for the #6AWG Neutral (white wire) because the other buses did not have any opening's big enough for the #6, at least it didn't look like it would fit...

I used #6AWG THHN for all 3 conductors and #10AWG THHN green for the ground, and these are are conveyed in the Steel Flex 3/4" you can see coming in from underneath. I installed bushings in the FMC where they connect to the compression fittings. The Sub panel Neutral is Isolated. This is fed from a 50 Amp (Connecticut Electric UBITBA250 Challenger “A” Series Circuit Breaker, 2-Pole 50-Amp) housed in the main. Which used to house a 30 amp for an old electric dryer circuit no longer in use. I had to source breakers for this old Challenger panel and they were pricey.

It's mounted to a 3/4" plywood board that is then fastened to the studs. The main is a 100 AMP service and according to the usage calculations for the house I'm well within that. Most big appliances are gas. I needed more outlets in the garage for my dust collector and table saw.

I live in San Francisco. The Panels are located in the garage at street level. Plan is to run 1/2" emt to job boxes along the workbench top, protected with GFCI outlets. I may at a later time install a 220 for the dust collector and a welder, which is why I went 50 amp.

So am I gonna burn the place down?
 

Attachments

  • main_sub.JPG
    main_sub.JPG
    87.4 KB · Views: 3
  • grnd.JPG
    grnd.JPG
    109.2 KB · Views: 3
  • brkr.JPG
    brkr.JPG
    112.2 KB · Views: 3
  • pnlbk.JPG
    pnlbk.JPG
    58.5 KB · Views: 3
  • sub.JPG
    sub.JPG
    83.5 KB · Views: 3
I am closing this thread, in accordance with the Forum Rules.

This site is designed for:


  • Contractors
  • Electricians
  • Engineers
  • Inspectors
  • Instructors
  • Other electrically related individuals

* This NEC Forum is for those in the electrical and related industries. Questions of a "How-To" nature by persons not involved in the electrical industry will be removed without notice.
If you feel this action to be in error, feel free to contact me via PM to explain.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 
Status
Not open for further replies.
Top