U uriel4pwr New member Aug 6, 2006 #1 How do you determine good insulation and bad insulation using a hand crank megaohmeter? Is there a chart somewhere in the NEC that tells you the minimum resistance of 500 mcm wire with XHHW insulation?
How do you determine good insulation and bad insulation using a hand crank megaohmeter? Is there a chart somewhere in the NEC that tells you the minimum resistance of 500 mcm wire with XHHW insulation?
zog Senior Member Location Charlotte, NC Aug 7, 2006 #2 NETA MTS and ATS has that info. www.netaworld.org If you post more details about the cable I can give you more specfic info
NETA MTS and ATS has that info. www.netaworld.org If you post more details about the cable I can give you more specfic info