Chayvo
Member
- Location
- Kazakhstan
I have a 480V supply and need to connect a light fixture which can be wired 277V. It was suggested to take a phase and ground to get 277V,Ive never done this before, is this a safe accepted method?
Don't have my code book for a direct reference, but it's the part(s) about not using the ground connection as a current carrying conductor. Neutral is a current carrying conductor, even though it is common to ground at the service entrance point. For you to use 277V at a lighting load from a 480/277V 4wire system, you will need the Neutral conductor run out to it from the service panel. You cannot just connect one phase to ground.Canton,
Where wouldI find this in the code to be able to support this?