No, but why not make it easy on everyone. go out and buy a box of green ground screws and these problems will not come upIs there any specific requirement in the code that says you must use a green grounding screw in a junction box?
Why buy screws when the one holding the spare clamp works fine (once the clamp is removed)Originally posted by Jhr:
No, but why not make it easy on everyone. go out and buy a box of green ground screws and these problems will not come up.
I don't have my 2005 handy but I believe 250.148(C) only applies to the screws used on devices. (the factory installed grounding screw)Originally posted by Jhr:
Now the question and thus the unnecessary problem, is this type of screw code compliant according to 250.148 (C).
I disagree 250.148 (C): "A connection shall be made between the one or more equipment grounding conductors and a metal box by means of a grounding screw that shall be used for no other pupose or a listed grounding device". This part does not mention a wiring device, this would be in a metal box with or without a device, such as a 4sq box with a blank plate where splices are made.The only place that a green screw is mentioned is 250.148(C) which only applies to devices.
Hey cut me some slack I was going from memory.Originally posted by Jhr:
I disagreeThe only place that a green screw is mentioned is 250.148(C) which only applies to devices.
250.126 Identification of Wiring Device Terminals.
The terminal for the connection of the equipment grounding conductor shall be identified by one of the following:
(1) A green, not readily removable terminal screw with a hexagonal head.
(2) A green, hexagonal, not readily removable terminal nut.
(3) A green pressure wire connector. If the terminal for the grounding conductor is not visible, the conductor entrance hole shall be marked with the word green or ground, the letters G or GR, a grounding symbol, or otherwise identified by a distinctive green color. If the terminal for the equipment grounding conductor is readily removable, the area adjacent to the terminal shall be similarly marked.
FPN: See FPN Figure 250.126.
And if they can't should they become electricians?Originally posted by pierre:
It would be pretty hard, even for apprentices in this industry to not understand the purpose of the screw that terminates the EGC to the enclosure.
I'm not sure about that. CMP5 doesn't know the purpose of that screw based on the code wording. It is a bonding and not a grounding screw.And if they can't should they become electricians?
That is correct but I wasn't implying that it applied to grounding screws. Someone asked about where in the code is the word green mentioned. I was just providing one article, which happens to be the one that I hear a lot when someone tells me (incorrectly) that the grounding screw in the metallic box must be green.That section is for devices, not for terminations to the metallic boxes.
I never posted that, Don if you read my first reply I agree that a green screw is not necessary, the only thing I will stand by is , why not use a green screw in these boxes, cuts out a lot of hassling over is it a ground screw or not, one other thing I agree it should be called a bonding screw, that is what is done when these screws are used.jhr,
Where does that section say "green"? The word "grounding" does not specity a type of screw
I don't see what's confusing about what the screw on the bottom of the box with an EGC on it is.By Jhr:
why not use a green screw in these boxes, cuts out a lot of hassling over is it a ground screw or not,