I got a school I am bidding on Says NO FMC unless for vibration- like transformer-ext, MC is strictly forbidden. I have to use EMT - Would a fixture whip. bypass this if it came with it- Or do I have to hard pipe to every light. Or do light vibrate lol-
The schools I have worked on and designed, allowed up to a 6' whip, but it cannot be MC, it has to be 3/8" flexible conduit, a couple were a 1/2" minimum flexible conduit. I would RFI it for clarification.
 