Judgement calls
Judgement calls
Nice guy, knowledgeable
Ok the questions came up
did you do the calcs for the main?
Well it was green tagged in 1959 and I don’t want to change the 200a main disco.
#6 wire? The smallest service is 100amp now
Apartments are allowed 60a and we have the wire for it.
Let’s get the Code section for that.
3 wire feeders
Dennis didn’t seem to think that using the neutral for the ground was too bad.
And when was it disallowed to grab the first 5’ of the water for a sub panel? 1990?
The expense of redoing the feeders will make the choice between pulling new wire or leaving the fp disco and sp there.
They wouldn’t trip no matter how much SParking was going on in the clothes closet The panel is located now.
Obviously were going to flip that around to face the living room so it’s just improvement after improvement
We don’t want to open a quantity of Sheetrock that would trigger a requirement to install sprinklers!
To pull new wire we would have to open up walls in 3 units.
I guess I can go up and over the roof and come down into the apartment but all the little distribution wires to the outlets and receptacles are all two wire anyway.
What a hardship just to replace an FP panel
Two wire distribution to the point of use outlets
I would say that the combination GFI and AFC I breakers would prove adequate here and
I would put the GFI at each point of use as possible for redundancy.
The only place not to have a GFI at point of use would be the switched outlet because there are no ceiling lights only switched outlets.
It can’t really be true that to change out a dangerous FP SubPanel and FP disconnect you would have to yank out all the old distribution wire and feeders
and install fire sprinklers for the building
and upgrade the meter main disconnect
That’s just too much of a hardship and it’s crazy
I would classify this is more of a repair of obsolete and inadequate equipment
Judgement calls
Nice guy, knowledgeable
Ok the questions came up
did you do the calcs for the main?
Well it was green tagged in 1959 and I don’t want to change the 200a main disco.
#6 wire? The smallest service is 100amp now
Apartments are allowed 60a and we have the wire for it.
Let’s get the Code section for that.
3 wire feeders
Dennis didn’t seem to think that using the neutral for the ground was too bad.
And when was it disallowed to grab the first 5’ of the water for a sub panel? 1990?
The expense of redoing the feeders will make the choice between pulling new wire or leaving the fp disco and sp there.
They wouldn’t trip no matter how much SParking was going on in the clothes closet The panel is located now.
Obviously were going to flip that around to face the living room so it’s just improvement after improvement
We don’t want to open a quantity of Sheetrock that would trigger a requirement to install sprinklers!
To pull new wire we would have to open up walls in 3 units.
I guess I can go up and over the roof and come down into the apartment but all the little distribution wires to the outlets and receptacles are all two wire anyway.
What a hardship just to replace an FP panel
Two wire distribution to the point of use outlets
I would say that the combination GFI and AFC I breakers would prove adequate here and
I would put the GFI at each point of use as possible for redundancy.
The only place not to have a GFI at point of use would be the switched outlet because there are no ceiling lights only switched outlets.
It can’t really be true that to change out a dangerous FP SubPanel and FP disconnect you would have to yank out all the old distribution wire and feeders
and install fire sprinklers for the building
and upgrade the meter main disconnect
That’s just too much of a hardship and it’s crazy
I would classify this is more of a repair of obsolete and inadequate equipment