• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

GREEN GROUND SCREW

Merry Christmas
Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: GREEN GROUND SCREW

jro,
as for 500 kcmil you still have to use a listed product to terminate any large wire,
That is the intent of 250.8. The wire termination itself must be a listed product, the screw or bolt used to connect the wire termination to the box is not required to be a listed product. Just like the bolts use to connect buss bar are not listed for that use.
Don
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: GREEN GROUND SCREW

Fro stranded grounding pigtails, I make my own with a crimp on, non insulated fork connector. Pretty fast to make up a bunch all at once
 
G

Guest

Guest
Re: GREEN GROUND SCREW

Do you use listed connectors and listed ratcheting crimpers, or do you just use the Panduits and a cheapie, cheapie crimper?
 

ryan_618

Senior Member
Re: GREEN GROUND SCREW

Originally posted by awwt:
Do you use listed connectors and listed ratcheting crimpers, or do you just use the Panduits and a cheapie, cheapie crimper?
I might get kicked around for this, but...like I said before, why sweat the small stuff? I think we have enough to worry about without things like listed ratcheting crimpers.

Wayne: This isn't a shot at you, just a general statement.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: GREEN GROUND SCREW

I have a set of the listed ratcheting crimpers, but they are for insulated terminals. I'm using non-insulated terminals, and the standard T&B Stay-kon WT111 works great.
By the way, in certain industries such as nuclear power, ratcheting crimpers have to be calibrated, as they sweat the small stuff. The incorrect crimp tool can cause the connection to fail. We don't see this too much with 120V loads, but I have seen many failed crimps on police cars and rescue rigs due to higher current at 12V. Some of the light bars will draw 20 to 40 amps.
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: GREEN GROUND SCREW

Tom interesting to hear you say that. The telcoms I have worked for all require calibrated crimpers such as the T&B WT111, TBM-8 TBM-25, TBM-14, etc. They even go as far as each crimp is inspected for proper termination. I have seen a many installers and electricians escorted out the door using unapproved or out of calibrations date crimpers. You hit the nail on the head, low voltage DC, but it is carried on to the AC and grounding systems.
 
Status
Not open for further replies.
Top