I have green roof project in NYC, above 11th floor. The roof will have an irrigation controller Pro-C Controller by Hunter Industries Incorporated (https://www.hunterindustries.com/irrigation-product/controllers/pro-cr).
Transformer output is 24 VAC and 1A (from controller to control valves). The spec doesn’t mention any circuit class 1/2/3.
My assumption is that I should use article 720 (from controller to 24 VAC control valves).
a. Cable can be only 2 wires (no ground).
b. Cable should be sunlight resistant and for wet locations.
c. Conduit is not mandatory required.
d. 720.4 Conductors. Conductors shall not be smaller than 12 AWG copper.
e. 720.11 Cables shall be supported by the building structure in such a manner that the cable will not be damaged by normal building use.
Did I miss something?