The green wire nuts are actually manufactured to comply with a different, more stringent, UL standard than are regular wire nuts.
db
Barclayd has this correct. There are at least 2 different standards for Wirenuts.
Standard Wirenuts are manufactured to UL Standard 486C
Green Wirenuts are manufactured to.....UL Standard 467
250.8 generally requires listing of grounding terminations.
I brought this up sometime last year on this forum. At the 2009 Eastern Section Meeting, UL made mention of this situation. It goes something like this:
Standard Wirenuts are not listed to UL 467. Remember that during a fault, the amount of current the green wirenuts sees, is the same as the current a standard wirenut sees. So, the manufacturers have not paid to have all of their wirenuts tested/evaluated for grounding purposes, with only the ones we see green as listed/evaluated. It saves them and us in the field a lot of money. Yet, most of us, if not all of us will and can use a standard wirenut with the EGC termination. The same goes for crimps. If you take a look at the Ideal product catalog, you will notice that they do not show any grounding conductors with standard wirenuts. This is on purpose, not a coincident. Call and ask any Ideal tech and they will explain it to you better than I did.
**Also, if one is installing a green wirenut, remember to pass one of the conductors through the hole in the wirenut. If you do not, you are not following the listing instructions.