Greenfield or cut 90 elbow to connect to panel

DaSnake

Member
Location
NYC
I'm adding a sub-panel on the 1st floor to clean up all the old circuits that run from the basement to the 1st floor. 1 1/4" EMT. I'd like to connect at the panel with a 90el but I'd need to cut one leg of the 90 to fit under the joists. The cut line looks like it's close to the bend radius so I might not be able to seat a set screw connector properly. Should I just hit the easy button and use a short piece of greenfield? See pics.
 

Attachments

  • IMG_5430.JPG
    IMG_5430.JPG
    1.4 MB · Views: 45
  • IMG_5431.JPG
    IMG_5431.JPG
    1.5 MB · Views: 44
Can't you shorten the horizontal run so that the el comes down the side of the panel then use an LB into the panel side?

-Hal
Good idea. I'm not sure I can physically pull three #3 wires, and one #6 thru an LB attached to the panel. I'll give it a try.

My other idea was to cut the 90el and use a short body compression coupling. The nut is able to slide up to my cut line. See pic...
 

Attachments

  • IMG_5432.JPG
    IMG_5432.JPG
    1.6 MB · Views: 3