synchro
- Chicago, IL
- EE
I think another limitation with connecting grid-tie inverters to a generator is that these inverters rely on the grid impedance to be very low so that it maintains a relatively clean voltage waveform in the presence of distortion in the PWM output current of the inverter. The higher the impedance of the source, the more distortion voltage will be developed for a given level of distortion current. Too much voltage distortion can adversely affect loads such as lighting, electronics, etc. An oversized generator will have a lower impedance and therefore result in a lower level of voltage distortion, but even so the impedance will very likely be larger than that from the POCO service. Passive and active filtering techniques could reduce the amount of inverter output current distortion, but that comes at a cost.This is describing the operation of a PV assist generator supply system to a large commercial load. These have been around for a while and do not apply to the standard residential load. They require that the generator be sized to supply 100% of the load when in backup mode and that the PV system is sized to no more than 35% of the load. The load cannot be allowed to drop below the level of the PV system output, which is why the PV output is limited. If it does the generator and PV system will be damaged. So the load needs to have a high minimum value during any time the PV system is in production. These can be made to work where the load has a constant high demand but that's not usually a residential system.
As others have said, incorporating an ESS eliminates a number of constraints and adds a lot of capability. Also it allows the generator to be run at higher loading levels where the engine is more efficient and then shut off when the ESS and PV can take over.