Got two inspected this year, using load-side interlock.
The portable generators void SolarEdge inverter warranty, so solar DC must be opened with main, at same time geny DC is closed.
AHJ's have no clue, not aware of inverter listing violation with generators, and never seen interlock listed for 3 switches.
Interlock OEM had to produce NRTL letter, but recalcitrant AHJ's stand firm, citing NEC 110.3(C) due to NTRL no longer certified.
Passing inspection requires proof that NRTL was certified at time test results were issued to interlock manufacturer (OEM).
Among 141 UL research documents, and correspondence related to certification status of NRTL in question, only 2 sentances provide relavant proof. It was a needle in the haystack, but I got the proof.
Orange County Public Works AHJ remained none responsive, until legal proof settled NRTL certification at specific dates indicated, and was provided to the Building Official at the State capital in Sacramento.