Has any one installed a backup generator that was grid tied? I have a client asking about this but I have never seen or heard of one.
Thanks!
When you say "grid tied", do you mean that the power authority may, from time to time, ask your customer to push power into the public grid?
Has any one installed a backup generator that was grid tied? I have a client asking about this but I have never seen or heard of one.
Thanks!
Yeppers. One that would provide power during an outage or be able to push power back on to the grid when requested.
I don't know why a utility would want that; unless the generator is huge it wouldn't make a significant difference to the grid. Synchronization would be a prime consideration, of course.
The idea here is to be able to sell back to the grid during peak demand times, when that ability becomes an option.
A single home selling back at erratic times won't be of use to any one. But, if the grid operator knows in 5-15 minutes he is going to need X MW's of peak production for 2 minutes and they can turn on all the gensets in a particular area aggregate their poroduction and accomodate that short peak demand.
The cost of gas v. the cost of electricity is not of concern at this job at this point in time.
The only setups I have ever seen are homes with a typical ATS and Data Centers with UPS support in place for the transition. Nothing synchronized with the grid.
The idea here is to be able to sell back to the grid during peak demand times, when that ability becomes an option.
A single home selling back at erratic times won't be of use to any one. But, if the grid operator knows in 5-15 minutes he is going to need X MW's of peak production for 2 minutes and they can turn on all the gensets in a particular area aggregate their poroduction and accomodate that short peak demand.
The cost of gas v. the cost of electricity is not of concern at this job at this point in time.
The only setups I have ever seen are homes with a typical ATS and Data Centers with UPS support in place for the transition. Nothing synchronized with the grid.
You'll have to check your state regulations. To my knowledge most of them don't allow net metering for non-renewable sources.
What is your customers capacity?
This little experiement would be... sanctioned.
He has an 11kW generator, 1P 120/240V.
This little experiement would be... sanctioned.
He has an 11kW generator, 1P 120/240V.
Rectify the generator output to DC and feed a grid tie inverter? Not sure how to handle the MPPT input though.At that size, I seriously doubt any BPU will entertain a grid tie to push power into the grid, not the least because I doubt your standard 11 KW Generac comes with any provision for syncing with the grid, and such an option if available would likely be many times the cost of the generator itself. Also, I'm sure the manufacturer would walk/run away from having anything to do with this lash-up.