Most call that a lift station.Not really a septic but similar. It's just a holding tank before it gets pumped into the city sewer system
You mentioned earlier that locally you do accept that plug as the disconnecting means. Strictly based on NEC though I fail to see how that meets the requirements for motor and/or controller disconnecting means if it is inside that enclosure. Wouldn't it only be "in site from" when that enclosure is opened?A common method for household grinder pumps here is 12x12 PVC box with a receptacle mounted inside and a 2" PVC nipple to the pump well. The plug and associated float adapter are pulled thru the 2" and plugged in to the box receptacle. The 2" is sealed with various compounds.
Would you accept cord and plug connections as disconnecting means for any other motors/controllers if they were all located inside an enclosure on the supply side of each motor controller with no external operating means?