I don't understand what would compel you to run the EGC outside the conduit. Can you explain why?bekahhren said:No, I am definitely planning on running an EGC - the 6 awg bare in the trench (in the dirt itself I mean), but i just don't know whether code requires me to run another grounding conductor within the conduit itself...
Thanks!
bekahhren said:.......... to a backfed breaker at a main panel (at a house), with a ground rod at the array and the house.
This part of the post stuck in my mind so strongly I can't even think about the grounding.....alternative power supply controlled by a back-fed breaker ??? do I understand that correctly ?
don_resqcapt19 said:300.3(B) Conductors of the Same Circuit All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).