geochurchi
- Concord,NH
- Retired electrician
Hi All, is the Bond wire and equipment grounding the same conductor?
Bonded (Bonding). Connected to establish electrical continuity
and conductivity.
Bonding Conductor or Jumper. A reliable conductor to
ensure the required electrical conductivity between metal
parts required to be electrically connected.
Bonding Jumper, Equipment. The connection between two
or more portions of the equipment grounding conductor.
Bonding Jumper, Main. The connection between the
grounded circuit conductor and the equipment grounding
conductor at the service.
Bonding Jumper, System. The connection between the
grounded circuit conductor and the supply-side bonding
jumper, or the equipment grounding conductor, or both, at a
separately derived system.
Grounding Conductor, Equipment (EGC). The conductive
path(s) installed to connect normally non–current-carrying
metal parts of equipment together and to the system grounded
conductor or to the grounding electrode conductor, or both.
Informational Note No. 1: It is recognized that the equipment
grounding conductor also performs bonding.
Informational Note No. 2: See 250.118 for a list of acceptable
equipment grounding conductors.