Don
Don
.
By running a EGC along with a GC tapped from the same point, [Xfmr or service] in the same raceway will create a code violation and provide parallel paths/loop between source and main/MDP/CBP etc.
The GC or neutral can only be used for grounding/bonding on the "line" side of a service or separately derived system. Thats the code. In the past we had a couple of exceptions with ranges and dryers etc.
Somebody figured it out back in the 99 cycle and the code was changed and inpectors in my area will not allow a EGC running side by side with a GC from a service or XFMR to a MDP/MD/CBP etc.
We used to run a EGC and GC together in such cases, but whats the point, for they are the same conductor and thus they "split" load and thats why the OP has his concerns about is meter registering current on a EGC.
P.S. we bond the XFMR case to the GC with a jumper inside the XFMR.
Don
.
By running a EGC along with a GC tapped from the same point, [Xfmr or service] in the same raceway will create a code violation and provide parallel paths/loop between source and main/MDP/CBP etc.
The GC or neutral can only be used for grounding/bonding on the "line" side of a service or separately derived system. Thats the code. In the past we had a couple of exceptions with ranges and dryers etc.
Somebody figured it out back in the 99 cycle and the code was changed and inpectors in my area will not allow a EGC running side by side with a GC from a service or XFMR to a MDP/MD/CBP etc.
We used to run a EGC and GC together in such cases, but whats the point, for they are the same conductor and thus they "split" load and thats why the OP has his concerns about is meter registering current on a EGC.
P.S. we bond the XFMR case to the GC with a jumper inside the XFMR.