Ground and neutral bus

Status
Not open for further replies.

state159

Member
Location
Georgia
Is it acceptable to mix the bare ground wires and the neutrals (white) on the same ground bus (and vice versa on the neutral bus) in a 200 amp Square D Homeline distribution panel? Both buses are bonded to ground.
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: Ground and neutral bus

At the risk of being thought of as quarrelsome may I suggest that the term sub panel not be used since it has no generally accepted definition. What I think would be clearer is to ask if the panel is service equipment or is it supplied by a feeder.
--
Tom
 
Location
Florida
Re: Ground and neutral bus

On some panels that I've seen the manufactor instuction sticker in the panel. Saying for the neutral / equipment grounding bar 2 conductors of the same size under 1 hole and I believe if memory serves no larger then #10 wire
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Re: Ground and neutral bus

NFPA inspection manual. PP147

Figure 6.19 Distribution arrangement in Which Feeders Supply Two Subpanels.

"Subpanels" :eek:

Mike P.
 

bennie

Esteemed Member
Re: Ground and neutral bus

In my 1899 edition of a civil and electrical engineering book, the term "supplementary switchboard" is used to describe additional switchboards.

It also states "these are normally constructed of wood, but due to the possibility of ignition, slate and soapstone products are being used for back boards now days".

Non-conductive material was the preference for safety from shock.
 