djtazjr, the neutral never floats. In a SDS the neutral is bonded to a GEC, then the EGC's are ran with the grounded and ungrounded conductors.
In a non SDS, that Ed has diagrammed, the neutral is bonded to the GEC at the service panel. Look a little closer at the drawings.
Fault current in a non SDS has to flow back through the service panel MBJ, then to the generator neutral buss.