Ground Bar on Outside of Meterbase for CATV

Status
Not open for further replies.
Not to beat this thing up but, How thick does the metal have to be to have 2 threads fully engaged and not have to use nuts on the back side.
I would think a meter can is not thick enough to have 2 full threads engaged where you could use a self tap or self drilling screw without nuts on the backside.
 
Not to beat this thing up but, How thick does the metal have to be to have 2 threads fully engaged and not have to use nuts on the back side.
I would think a meter can is not thick enough to have 2 full threads engaged where you could use a self tap or self drilling screw without nuts on the backside.


You are correct, you would need to use a tap and a machine screw.

Roger
 
How thick does the metal have to be to have 2 threads fully engaged and not have to use nuts on the back side.
Well, a 6-32 or 8-32, with 32 threads per inch, would require the metal to be at least 1/16".
 
Here is the definition. The proposal was from the Telecom association. Its a great rule.
Intersystem Bonding Termination. A device that provides a means for connecting communications system(s) grounding conductor(s) and bonding conductor(s) at the service equipment or at the disconnecting means for buildings or structures supplied by a feeder or branch circuit.
 
I have not heard of any inspector requiring it, but is exactly what I did when I built my last home. The bare #4 runs out the bottom of the meter can, is welded to the ground bar, at the opposite end of the bar is another #4 welded and goes straight down to the GES.

My CATV block mounts directly on the ground bar, and The Telco NIU is mounted right next to the ground bar with a copper strap welded to the ground bar and terminated to the NIU ground stud.
 