Ground between electrical entrance and sub-panel.

Is a ground required form the electrical service entrance to the sub panel if the sub panel is the first point of distribution?
To answer what seems to be the question, if the "service entrance" means a main breaker, yes, you need a 4-wire feeder and non-bonded neutral in the distribution panel. Is this a modification to an existing installation or is it new work?
 